Voltage Drop Calculator

Estimate the voltage drop in copper and aluminium cables. Free, fast and easy to use.

Calculator

Result 4.56 VVoltage drop
Voltage drop (%)
1.98%
Voltage at the load
225.4 V

How it works

Voltage drop grows with cable length and current and falls with a larger cross-section. The calculator uses conductor resistivity at about 20 °C and ignores reactance, which is accurate enough for typical small installations. Many standards recommend keeping the drop below 3–5 %.

Formula

DC, AC 1~: ΔU = 2 × L × I × ρ / A
AC 3~: ΔU = √3 × L × I × ρ / A
ρ Cu = 0.0178, ρ Al = 0.0282 Ω·mm²/m

Worked examples

  • Circuit type: AC single-phase · Voltage (V): 230 · Current (A): 10 · Cable length, one way (m): 30 · Conductor cross-section (mm²): 1.5 · Conductor material: Copper → Voltage drop: 7.12 V
  • Circuit type: AC three-phase · Voltage (V): 400 · Current (A): 32 · Cable length, one way (m): 50 · Conductor cross-section (mm²): 6 · Conductor material: Copper → Voltage drop: 8.22 V
  • Circuit type: DC · Voltage (V): 12 · Current (A): 10 · Cable length, one way (m): 5 · Conductor cross-section (mm²): 4 · Conductor material: Copper → Voltage drop: 0.45 V

Calculations run locally in your browser. Results are for information only — for engineering, electrical or financial decisions, verify the assumptions and applicable standards.

Frequently asked questions

What voltage drop is acceptable?

Many standards recommend at most 3 % for lighting circuits and 5 % for other circuits, from the supply point to the load.

How can I reduce voltage drop?

Use a larger cross-section, a shorter cable or a higher voltage. Copper has a lower voltage drop than aluminium of the same cross-section.